Originally Posted by Kolyan2k View Post
Yeah not something you want to do yourself if you have those questions.....
But anyway, 1. You need to replace breaker at panel and get rid off the disconnect outside and install proper outside fitting and a box that supposed to take 110v outlet (and need bubble cover). 2. Yes, just cap it. 3. I would install GFCI breaker at panel and regular outlet outside. You also need to reduce the wire size ends, I doubt you can get 50amp wire properly secure at outlet and at the breaker.
The cable that you ran underground also need to be made for underground, you cant just run any cable.
Yeah I figured I would have to mess with the main panel, I don't really want to mess with that so will either disconnect the cables going out of the box in the patio (just for added safety it's obviously switched off at both breakers and the disconnect removed) and keep my extension cord setup, or get a pro to check it out. At this point I guess my main concern is the pros not wanting to work on it without digging up the cables we ran which I have no desire to do, that was a big project.